Question 3003 of 153 · Oklahoma Fire Alarm Technician Exam

A spot-type heat detector is mounted on a sidewall. What mounting zone is permitted?

Exactly one answer is correct.

Show solution

Correct answer to question 3003

  • A: Between 4 in and 12 in below the ceiling

Explanation

Sidewall heat detectors must be between 4 in and 12 in from the ceiling, measured to the top of the detector. Ceiling-mounted heat detectors must be at least 4 in from the sidewall.

Next to question ›