Question 3003 of 153 · Oklahoma Fire Alarm Technician Exam
A spot-type heat detector is mounted on a sidewall. What mounting zone is permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3003
- A: Between 4 in and 12 in below the ceiling
Explanation
Sidewall heat detectors must be between 4 in and 12 in from the ceiling, measured to the top of the detector. Ceiling-mounted heat detectors must be at least 4 in from the sidewall.
More questions: System Layout and NFPA 72 Requirements
- 3004A heat detector has a listed spacing of 50 ft. What is the maximum distance from a wall to the nearest detector on a smooth ceiling?
- 3005A heat detector with a listed spacing of 50 ft is installed on a smooth ceiling 15 ft high. Using the ceiling height reduction factor of 0.77 for ceilings over 14 ft up to 16 ft, what is the adjusted spacing?
- 3006On a solid joist ceiling, how is heat detector spacing measured at right angles to the joists adjusted?
- 3007Under a peaked ceiling, where must a row of spot-type smoke detectors be placed?
- 3008A heat detector should have a temperature rating at least how far above the maximum expected ambient ceiling temperature?
- 3009A heat detector frame is colored white. Which temperature classification does this color code indicate?