Question 3012 of 153 · Oklahoma Fire Alarm Technician Exam
What is the required mounting height for the operable part of a manual fire alarm box?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3012
- C: Between 42 in and 48 in above the floor
Explanation
The operable part of a manual fire alarm box must be not less than 42 in and not more than 48 in above floor level, which keeps it reachable for most people including wheelchair users.
More questions: System Layout and NFPA 72 Requirements
- 3013A manual fire alarm box serves an exit doorway. Within what distance of the doorway must it be located?
- 3014What is the minimum sound level for an audible public mode evacuation signal in an area with an average ambient sound level of 70 dBA?
- 3015What is the maximum sound pressure level permitted for an audible notification appliance at the minimum hearing distance?
- 3016A sleeping room has an average ambient of 35 dBA and a maximum 60 second level of 45 dBA. What is the minimum required audible signal level at the pillow?
- 3017What signal characteristic does NFPA 72 require for audible alarms intended to wake sleeping occupants in sleeping areas?
- 3018Which signal pattern is required for the standard fire evacuation tone?