A manual fire alarm box serves an exit doorway. Within what distance of the doorway must it be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3013
- A: 5 ft
Explanation
Manual fire alarm boxes are located within 5 ft of the entrance to each exit on every floor, so occupants pass one while leaving.
More questions: System Layout and NFPA 72 Requirements