What is the minimum sound level for an audible public mode evacuation signal in an area with an average ambient sound level of 70 dBA?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3014
- B: 85 dBA
Explanation
Public mode signals must be at least 15 dB above the average ambient sound level (or 5 dB above the maximum level lasting 60 seconds or more, whichever is greater). 70 + 15 = 85 dBA.