Using the room spacing table for a single wall-mounted strobe, what minimum effective intensity is required for a 20 ft by 20 ft room?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3023
- D: 15 cd
Explanation
The wall-mounted room spacing table assigns 15 cd to a 20 ft by 20 ft room with one appliance. Larger rooms need higher intensity, for example 30 cd for about 28 ft by 28 ft and 60 cd for 40 ft by 40 ft.
More questions: System Layout and NFPA 72 Requirements
- 3024A sleeping room strobe is mounted 18 in below the ceiling. What minimum effective intensity is required?
- 3025In a corridor not more than 20 ft wide, what is the maximum distance from the end of the corridor to the nearest visible appliance?
- 3026What is the minimum secondary power capacity for a protected premises fire alarm system without voice evacuation?
- 3027A fire alarm control unit is in an area that is not continuously occupied. What does NFPA 72 require at that location?
- 3028Within what time after an initiating device activates must the fire alarm control unit activate the alarm notification appliances?
- 3029What is the maximum time permitted for alarm verification on a smoke detector circuit?