Power limited fire alarm cable run vertically in a shaft between floors must at least be which type?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4007
- D: FPLR
Explanation
Riser rated FPLR cable is required in vertical runs in shafts between floors. FPLP (plenum) is also acceptable as a substitute, but general purpose FPL is not.
More questions: Installation, Wiring and Pathways
- 4008How must the branch circuit disconnecting means for a fire alarm control unit be marked?
- 4009Two wire smoke detectors powered from an initiating device circuit must meet which requirement?
- 4010On a conventional Class B initiating device circuit, a T-tap is added to reach an extra detector. What problem does this create?
- 4011How must power limited fire alarm cable above a suspended ceiling be supported?
- 4012May power limited fire alarm conductors share a raceway with 120 V branch circuit conductors?
- 4013What makes a fire alarm circuit a power limited fire alarm (PLFA) circuit?