Question 4010 of 153 · Oklahoma Fire Alarm Technician Exam
On a conventional Class B initiating device circuit, a T-tap is added to reach an extra detector. What problem does this create?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4010
- B: Devices on the tap are not supervised, since a break there is not reported
Explanation
Supervision depends on current flowing through every device to the end of line resistor. A T-tap branch has no supervision current, so an open on the tap goes unnoticed.