How must the branch circuit disconnecting means for a fire alarm control unit be marked?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4008
- B: Red marking, identified as FIRE ALARM CIRCUIT, and accessible only to authorized personnel
Explanation
The dedicated branch circuit disconnect must have a red marking, be identified as FIRE ALARM CIRCUIT and be accessible only to authorized personnel. Its location must be identified at the control unit.
More questions: Installation, Wiring and Pathways
- 4009Two wire smoke detectors powered from an initiating device circuit must meet which requirement?
- 4010On a conventional Class B initiating device circuit, a T-tap is added to reach an extra detector. What problem does this create?
- 4011How must power limited fire alarm cable above a suspended ceiling be supported?