Question 4011 of 153 · Oklahoma Fire Alarm Technician Exam
How must power limited fire alarm cable above a suspended ceiling be supported?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4011
- C: By the building structure, so normal use does not damage it
Explanation
Fire alarm cables must be supported by the building structure so normal building use does not damage them. Ceiling tiles and grid support wires are not an acceptable means of support unless specifically permitted.
More questions: Installation, Wiring and Pathways
- 4012May power limited fire alarm conductors share a raceway with 120 V branch circuit conductors?
- 4013What makes a fire alarm circuit a power limited fire alarm (PLFA) circuit?
- 4014Fire alarm cable is installed in a ceiling space used for environmental air (a plenum). Which cable type is required?
- 4015Which communications cable type may be substituted for FPLR riser cable?
- 4016What is the minimum conductor size permitted in a multiconductor power limited fire alarm cable?
- 4017What is the main purpose of the equipment grounding conductor connected to a fire alarm control unit?