May power limited fire alarm conductors share a raceway with 120 V branch circuit conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4012
- A: No, unless a barrier or an exception in Article 760 permits it
Explanation
Power limited fire alarm conductors are kept out of raceways, cables and enclosures that contain light, power, Class 1 or non power limited fire alarm conductors, unless separated by a barrier or covered by a specific exception.