Question 4012 of 153 · Oklahoma Fire Alarm Technician Exam

May power limited fire alarm conductors share a raceway with 120 V branch circuit conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 4012

  • A: No, unless a barrier or an exception in Article 760 permits it

Explanation

Power limited fire alarm conductors are kept out of raceways, cables and enclosures that contain light, power, Class 1 or non power limited fire alarm conductors, unless separated by a barrier or covered by a specific exception.