Question 5008 of 153 · Oklahoma Fire Alarm Technician Exam
After a software change on a fire alarm system, what portion of initiating devices not directly affected must be tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5008
- C: 10 percent, with a minimum of 1 and a maximum of 50
Explanation
All functions known to be affected are tested, plus 10 percent of the initiating devices not directly affected, at least one and up to 50, to confirm the change did not break other functions.