A smoke detector is planned for an unheated garage where winter temperatures fall to 20 F. What is the correct approach?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1015
- A: Use a device listed for that temperature or a different detector type
Explanation
Standard smoke detectors are not to be used below 32 F unless specifically listed for it. Heat detectors are the usual choice in unheated spaces. A dust cover or a different mounting height does not change the listed operating range.