You are mounting a combination horn/strobe on a wall. Which mounting rule controls its height?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1025
- A: The visible appliance rule, so the lens is 80 in. to 96 in. above the floor
Explanation
Combination audible/visible appliances on walls are installed to the visible appliance mounting requirements, with the whole lens between 80 in. and 96 in. A horn/strobe mounted only to the audible rule could end up with the lens above 96 in.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1026The drawings show ceiling-mounted strobes, but the installer looks up the candela rating in the wall-mounted spacing table. What is wrong?
- 1027A 40 ft x 40 ft room will be covered by one wall-mounted strobe. Using the NFPA 72 room spacing table, what is the minimum effective intensity?
- 1028A single wall-mounted strobe will cover a 20 ft x 20 ft office. What is the minimum effective intensity from the room spacing table?
- 1029Strobes are being installed in a corridor 10 ft wide and 150 ft long. Which layout meets the corridor rule of the 2022 edition?
- 1030What flash rate must a visible notification appliance used for fire alarm have?
- 1031When must strobes within a field of view be synchronized?