The drawings show ceiling-mounted strobes, but the installer looks up the candela rating in the wall-mounted spacing table. What is wrong?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1026
- A: Ceiling-mounted appliances have their own spacing table
Explanation
NFPA 72 has separate room spacing tables for wall-mounted and ceiling-mounted visible appliances, and the ceiling table also depends on ceiling height. Using the wrong table can leave a room under-lit.