The drawings show ceiling-mounted strobes, but the installer looks up the candela rating in the wall-mounted spacing table. What is wrong?

Exactly one answer is correct.

Show solution

Correct answer to question 1026

  • A: Ceiling-mounted appliances have their own spacing table

Explanation

NFPA 72 has separate room spacing tables for wall-mounted and ceiling-mounted visible appliances, and the ceiling table also depends on ceiling height. Using the wrong table can leave a room under-lit.