Question 1027 of 299 · NICET Fire Alarm Systems Level I
A 40 ft x 40 ft room will be covered by one wall-mounted strobe. Using the NFPA 72 room spacing table, what is the minimum effective intensity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1027
- A: 60 cd
Explanation
For a single wall-mounted appliance, the table lists 15 cd for a 20 ft x 20 ft room, 30 cd at 28 ft x 28 ft, 34 cd at 30 ft x 30 ft and 60 cd at 40 ft x 40 ft. A bigger room needs a brighter strobe or more strobes.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1028A single wall-mounted strobe will cover a 20 ft x 20 ft office. What is the minimum effective intensity from the room spacing table?
- 1029Strobes are being installed in a corridor 10 ft wide and 150 ft long. Which layout meets the corridor rule of the 2022 edition?
- 1030What flash rate must a visible notification appliance used for fire alarm have?
- 1031When must strobes within a field of view be synchronized?
- 1032What light color is required for public mode visible alarm appliances that signal a fire alarm?
- 1033Why must polarity be observed when terminating a horn/strobe on a notification appliance circuit?