Strobes are being installed in a corridor 10 ft wide and 150 ft long. Which layout meets the corridor rule of the 2022 edition?

Exactly one answer is correct.

Show solution

Correct answer to question 1029

  • B: Within 15 ft of each end and no more than 100 ft apart

Explanation

In the 2022 edition, corridors 20 ft wide or less may use 15 cd appliances located within 15 ft of each end, with no more than 100 ft between appliances. For a 150 ft corridor that means at least three strobes.