Strobes are being installed in a corridor 10 ft wide and 150 ft long. Which layout meets the corridor rule of the 2022 edition?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1029
- B: Within 15 ft of each end and no more than 100 ft apart
Explanation
In the 2022 edition, corridors 20 ft wide or less may use 15 cd appliances located within 15 ft of each end, with no more than 100 ft between appliances. For a 150 ft corridor that means at least three strobes.