On a conventional Class B initiating device circuit, how should the installer connect the wires at a smoke detector base?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1034
- C: Cut the wire and land the in and out conductors on separate terminals
Explanation
Breaking the conductor at each terminal means a loose wire or a removed device opens the circuit and causes a trouble signal. A conductor looped unbroken under one screw can come loose without the panel ever noticing.