Why must polarity be observed when terminating a horn/strobe on a notification appliance circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1033
- C: The appliance is polarized and the circuit is supervised in reverse polarity
Explanation
Most DC notification appliances have a built-in diode. During normal standby the panel supervises the circuit with reversed polarity, and in alarm it applies normal polarity. A reversed appliance will not operate correctly and can upset supervision.