Question 1028 of 299 · NICET Fire Alarm Systems Level I
A single wall-mounted strobe will cover a 20 ft x 20 ft office. What is the minimum effective intensity from the room spacing table?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1028
- D: 15 cd
Explanation
A 20 ft x 20 ft room needs at least 15 cd from one wall-mounted appliance. That is also the smallest standard rating commonly used.