Question 1070 of 299 · NICET Fire Alarm Systems Level I
How must the disconnecting means of the fire alarm branch circuit be marked?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1070
- D: Red, identified as FIRE ALARM CIRCUIT, and accessible only to authorized people
Explanation
The circuit disconnect must have a red marking, be identified as FIRE ALARM CIRCUIT and be accessible only to authorized personnel, often with a breaker lock. This prevents someone from switching it off by mistake.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1071Where must the location of the fire alarm branch circuit overcurrent device be recorded?
- 1072May the branch circuit for a fire alarm control unit be protected by a ground-fault circuit interrupter (GFCI)?
- 1073More than two conductors are pulled into a conduit. What maximum percentage of the conduit cross section may they fill?
- 1074Between pull points, what is the maximum total of bends allowed in an EMT run?
- 1075How must EMT be supported near a junction box?
- 1076Cable ties used to bundle fire alarm cables in a plenum must have which property?