Question 1073 of 299 · NICET Fire Alarm Systems Level I
More than two conductors are pulled into a conduit. What maximum percentage of the conduit cross section may they fill?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1073
- C: 40 percent
Explanation
NEC Chapter 9 Table 1 limits fill to 53 percent for one conductor, 31 percent for two and 40 percent for over two conductors. Too much fill damages insulation during the pull.