Question 1071 of 299 · NICET Fire Alarm Systems Level I

Where must the location of the fire alarm branch circuit overcurrent device be recorded?

Exactly one answer is correct.

Show solution

Correct answer to question 1071

  • C: Permanently identified at the fire alarm control unit

Explanation

The location of the branch circuit disconnect and its overcurrent device (panel and circuit number) must be permanently identified at the control unit, so a technician can find it quickly.

Next to question ›