Question 1072 of 299 · NICET Fire Alarm Systems Level I
May the branch circuit for a fire alarm control unit be protected by a ground-fault circuit interrupter (GFCI)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1072
- C: No, GFCI and AFCI protection are not allowed on this circuit
Explanation
The NEC does not allow the fire alarm branch circuit to be supplied through a GFCI or AFCI. A nuisance trip would silently remove primary power from the fire alarm system.