Which device is used to let the fire alarm system switch an external load, such as releasing door holders?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1142
- B: A control (relay) module
Explanation
Control or relay modules give the panel an output to switch other equipment, such as door holders, fan shutdown or elevator recall. Monitor modules are inputs.
More questions: Installation (Peripherals, Cabling, Job Site Safety)
- 1143Where must a relay or control module that performs an emergency control function, such as fan shutdown, be located?
- 1144A sprinkler system serves an elevator machine room and the elevator power is shunt tripped on waterflow. Where must the heat detectors for elevator shutdown be located?
- 1145When a technician mounts a smoke detector near a ceiling beam on a ceiling with deep beams, what must be checked before installation?
- 1146Which NFPA 72 pathway class is intended for Ethernet-type networks with redundant equipment paths?
- 1147An installer mounts a monitor module above a ceiling to watch a sprinkler tamper switch. What should be done so it can be found later?
- 1001A spot-type smoke detector has to be mounted on a sidewall instead of the ceiling. Where must the top of the detector be located?