Question 2006 of 299 · NICET Fire Alarm Systems Level I
What does a proper annual functional test of a spot-type smoke detector have to prove?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- B: That smoke can enter the chamber and the detector sends an alarm
Explanation
The functional test introduces smoke or a listed aerosol approved by the manufacturer to verify smoke entry into the sensing chamber and an alarm response. A blinking LED or magnet test does not prove smoke can get in.