Question 2007 of 299 · NICET Fire Alarm Systems Level I
How is a restorable spot-type fixed-temperature heat detector functionally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2007
- B: With a heat source as recommended by the manufacturer
Explanation
Restorable heat detectors are tested with a heat source per the manufacturer, for example a listed heat gun or hair dryer type tester, without damaging the detector. An open flame can damage the device and the ceiling.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2008Why is a heat test not done on a nonrestorable fixed-temperature heat detector?
- 2009Nonrestorable spot-type fixed-temperature heat detectors have been in service for 15 years. What is required?
- 2010A building has 300 nonrestorable spot-type heat detectors that are 15 years old. The owner chooses lab testing instead of replacement. How many detectors must be sent for testing?
- 2011How often are manual fire alarm boxes functionally tested?
- 2012How often are audible and visible notification appliances functionally tested?
- 2013How often must sprinkler waterflow alarm devices connected to the fire alarm system be tested?