Question 2025 of 299 · NICET Fire Alarm Systems Level I
At acceptance testing, how are installation conductors checked for unwanted voltages?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2025
- B: With a volt/ohmmeter to confirm there is no stray voltage
Explanation
Conductor testing at acceptance includes checking for stray voltage, ground faults, short circuits and loop resistance with suitable meters before devices are connected or with the circuit isolated.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2026To measure loop resistance of an initiating device circuit during acceptance testing, what is done at the far end of the circuit?
- 2027A technician checks fire alarm conductors for isolation from ground. What is being looked for?
- 2028You need to megger (insulation resistance test) a new fire alarm circuit. What must be done first?
- 2029When measuring the voltage on a notification appliance circuit with a multimeter, how is the meter connected?
- 2030When measuring current drawn by a strobe circuit with a multimeter, how is the meter connected?
- 2031Why must resistance measurements be made with the circuit de-energized?