Question 2026 of 299 · NICET Fire Alarm Systems Level I
To measure loop resistance of an initiating device circuit during acceptance testing, what is done at the far end of the circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2026
- D: The conductor pair is short-circuited at the far end
Explanation
With each conductor pair shorted at the far end, the resistance is measured and recorded from the panel end. It must not exceed the manufacturer's limits for that circuit.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2027A technician checks fire alarm conductors for isolation from ground. What is being looked for?
- 2028You need to megger (insulation resistance test) a new fire alarm circuit. What must be done first?
- 2029When measuring the voltage on a notification appliance circuit with a multimeter, how is the meter connected?
- 2030When measuring current drawn by a strobe circuit with a multimeter, how is the meter connected?
- 2031Why must resistance measurements be made with the circuit de-energized?
- 2032You disconnect a Class B initiating device circuit at the panel and measure across the pair. The meter shows about 4,700 ohm, matching the EOL value. What does this tell you?