Question 2028 of 299 · NICET Fire Alarm Systems Level I
You need to megger (insulation resistance test) a new fire alarm circuit. What must be done first?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2028
- D: Disconnect the circuit from the panel and all electronic devices
Explanation
An insulation tester applies a high test voltage, often 250 V to 500 V or more, that can destroy panel and device electronics. Isolate the conductors before testing.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2029When measuring the voltage on a notification appliance circuit with a multimeter, how is the meter connected?
- 2030When measuring current drawn by a strobe circuit with a multimeter, how is the meter connected?
- 2031Why must resistance measurements be made with the circuit de-energized?
- 2032You disconnect a Class B initiating device circuit at the panel and measure across the pair. The meter shows about 4,700 ohm, matching the EOL value. What does this tell you?
- 2033Measured across a disconnected Class B circuit pair, the meter shows OL (over limit). What is the most likely problem?
- 2034Across a disconnected initiating circuit pair, the meter reads close to 0 ohm. What is the most likely problem?