Question 2041 of 299 · NICET Fire Alarm Systems Level I
In sleeping areas, what minimum sound level is required at the pillow, besides the 15 dB over ambient rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2041
- B: 75 dBA
Explanation
Sleeping area signals must be at least 15 dB above average ambient, 5 dB above the maximum 60 second level, or 75 dBA, whichever is greater, measured at the pillow.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2042Which audible signal frequency is required for alarm signals that awaken sleeping occupants in sleeping areas where required by NFPA 72?
- 2043What is the maximum sound pressure level allowed for audible fire alarm signals?
- 2044Two horns each produce 80 dBA at a measuring point. What is the combined level at that point?
- 2045A horn measures 90 dBA at 10 ft in a free field. What level would you expect at 20 ft?
- 2046What pattern does the standard evacuation signal (temporal-3) use?
- 2047For a fire alarm system that is not a voice system, what secondary power capacity does NFPA 72 require?