What is the maximum sound pressure level allowed for audible fire alarm signals?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2043
- B: 110 dBA
Explanation
NFPA 72 limits the total sound pressure of audible signals to 110 dBA at the minimum hearing distance. Louder signals risk hearing damage; where more is needed, visible signals are used.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2044Two horns each produce 80 dBA at a measuring point. What is the combined level at that point?
- 2045A horn measures 90 dBA at 10 ft in a free field. What level would you expect at 20 ft?
- 2046What pattern does the standard evacuation signal (temporal-3) use?
- 2047For a fire alarm system that is not a voice system, what secondary power capacity does NFPA 72 require?
- 2048For an in-building emergency voice/alarm communications system, how long must the batteries run the system in alarm after 24 hours of standby?
- 2049A panel draws 0.25 A in standby and 2.0 A in alarm. Using 24 hours standby, 5 minutes alarm and the 1.25 aging correction factor required by NFPA 72 (2022/2025), what battery capacity is needed?