Question 2045 of 299 · NICET Fire Alarm Systems Level I
A horn measures 90 dBA at 10 ft in a free field. What level would you expect at 20 ft?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2045
- C: About 84 dBA
Explanation
In a free field, sound drops about 6 dB each time the distance doubles (inverse square law): 90 - 6 = 84 dBA. Real rooms with reflections may lose less.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2046What pattern does the standard evacuation signal (temporal-3) use?
- 2047For a fire alarm system that is not a voice system, what secondary power capacity does NFPA 72 require?
- 2048For an in-building emergency voice/alarm communications system, how long must the batteries run the system in alarm after 24 hours of standby?
- 2049A panel draws 0.25 A in standby and 2.0 A in alarm. Using 24 hours standby, 5 minutes alarm and the 1.25 aging correction factor required by NFPA 72 (2022/2025), what battery capacity is needed?
- 2050A small panel draws 0.150 A in standby and 1.2 A in alarm. Without a safety factor, what is the required battery capacity for 24 hours standby plus 5 minutes alarm?
- 2051How must storage batteries for a fire alarm system be marked?