For a fire alarm system that is not a voice system, what secondary power capacity does NFPA 72 require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2047
- C: 24 hours of standby, then 5 minutes of alarm
Explanation
The secondary supply must run the system under quiescent load for 24 hours and then operate all alarm notification appliances for 5 minutes. Emergency voice/alarm communications systems need 15 minutes of alarm instead.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2048For an in-building emergency voice/alarm communications system, how long must the batteries run the system in alarm after 24 hours of standby?
- 2049A panel draws 0.25 A in standby and 2.0 A in alarm. Using 24 hours standby, 5 minutes alarm and the 1.25 aging correction factor required by NFPA 72 (2022/2025), what battery capacity is needed?
- 2050A small panel draws 0.150 A in standby and 1.2 A in alarm. Without a safety factor, what is the required battery capacity for 24 hours standby plus 5 minutes alarm?
- 2051How must storage batteries for a fire alarm system be marked?
- 2052During the annual test, a sealed lead-acid battery cannot hold its voltage under load and falls below the manufacturer's limit. What should be done?
- 2053Two batteries in series supply a 24 V panel. One battery fails its test. What is good practice?