Question 2049 of 299 · NICET Fire Alarm Systems Level I

A panel draws 0.25 A in standby and 2.0 A in alarm. Using 24 hours standby, 5 minutes alarm and the 1.25 aging correction factor required by NFPA 72 (2022/2025), what battery capacity is needed?

Exactly one answer is correct.

Show solution

Correct answer to question 2049

  • D: 7.7 Ah

Explanation

Standby: 0.25 A x 24 h = 6.0 Ah. Alarm: 2.0 A x 5/60 h = 0.167 Ah. Total 6.167 Ah, times 1.25 = 7.7 Ah. Multiplying by 1.2 (the older 20 percent margin) gives 7.4 Ah, which is too low for the 2022 and 2025 editions. Choose the next standard size above 7.7 Ah, for example 8 Ah.