Question 2049 of 299 · NICET Fire Alarm Systems Level I
A panel draws 0.25 A in standby and 2.0 A in alarm. Using 24 hours standby, 5 minutes alarm and the 1.25 aging correction factor required by NFPA 72 (2022/2025), what battery capacity is needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2049
- D: 7.7 Ah
Explanation
Standby: 0.25 A x 24 h = 6.0 Ah. Alarm: 2.0 A x 5/60 h = 0.167 Ah. Total 6.167 Ah, times 1.25 = 7.7 Ah. Multiplying by 1.2 (the older 20 percent margin) gives 7.4 Ah, which is too low for the 2022 and 2025 editions. Choose the next standard size above 7.7 Ah, for example 8 Ah.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2050A small panel draws 0.150 A in standby and 1.2 A in alarm. Without a safety factor, what is the required battery capacity for 24 hours standby plus 5 minutes alarm?
- 2051How must storage batteries for a fire alarm system be marked?
- 2052During the annual test, a sealed lead-acid battery cannot hold its voltage under load and falls below the manufacturer's limit. What should be done?
- 2053Two batteries in series supply a 24 V panel. One battery fails its test. What is good practice?
- 2054To test the transfer to secondary power, the technician switches off the AC branch circuit. What should happen?
- 2055On a control unit, what is the difference between silencing and resetting?