Question 2051 of 299 · NICET Fire Alarm Systems Level I
How must storage batteries for a fire alarm system be marked?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2051
- D: With the month and year of manufacture
Explanation
Batteries are marked with their month and year of manufacture, which lets the technician judge battery age during inspection and plan replacement.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2052During the annual test, a sealed lead-acid battery cannot hold its voltage under load and falls below the manufacturer's limit. What should be done?
- 2053Two batteries in series supply a 24 V panel. One battery fails its test. What is good practice?
- 2054To test the transfer to secondary power, the technician switches off the AC branch circuit. What should happen?
- 2055On a control unit, what is the difference between silencing and resetting?
- 2056What signal type does a fire alarm panel use to report a fault in the system, such as an open circuit?
- 2057A sprinkler control valve has been closed. What type of signal should the panel show?