Question 2052 of 299 · NICET Fire Alarm Systems Level I
During the annual test, a sealed lead-acid battery cannot hold its voltage under load and falls below the manufacturer's limit. What should be done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2052
- A: Replace the battery
Explanation
Batteries that fail the load or voltage test are replaced per the manufacturer's recommendations. Sealed (VRLA) batteries cannot be refilled, and a panel without working batteries has no secondary power.