A waterflow alarm comes in every time the city water pressure surges, without any real flow. What adjustment is most likely needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2087
- A: Check the waterflow switch retard setting
Explanation
The retard delays the signal so short surges do not cause false alarms. It must still keep the total time to alarm within 90 seconds.