A household smoke alarm in an apartment was manufactured 11 years ago. What should be done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2089
- A: Replace it
Explanation
Smoke alarms are replaced no later than 10 years after the date of manufacture, or sooner if they fail an operability test or the manufacturer says so.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2090During acceptance testing of a Class A initiating circuit, how is the redundant path proven?
- 2091How is ground fault supervision of a circuit verified during acceptance testing?
- 2092Within what time must a battery charger be able to recharge fully discharged fire alarm batteries?
- 2093A smoke detector is marked with a listed sensitivity range of 1.0 to 3.5 percent per foot obscuration. The test reads 3.9 percent per foot. What does this mean?
- 2094An addressable panel prints sensitivity readings for every smoke detector. May this be used for the required sensitivity test?
- 2095What qualification does NFPA 72 expect from people who inspect, test and maintain fire alarm systems?