What is the reason for testing carbon monoxide detectors per their manufacturer's instructions instead of with smoke aerosol?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2088
- C: They sense CO gas, so they need a CO test method
Explanation
CO detectors respond to carbon monoxide gas. They are tested per the manufacturer, often with a listed test gas or test function. Smoke aerosol does not verify the CO sensor.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2089A household smoke alarm in an apartment was manufactured 11 years ago. What should be done?
- 2090During acceptance testing of a Class A initiating circuit, how is the redundant path proven?
- 2091How is ground fault supervision of a circuit verified during acceptance testing?
- 2092Within what time must a battery charger be able to recharge fully discharged fire alarm batteries?
- 2093A smoke detector is marked with a listed sensitivity range of 1.0 to 3.5 percent per foot obscuration. The test reads 3.9 percent per foot. What does this mean?
- 2094An addressable panel prints sensitivity readings for every smoke detector. May this be used for the required sensitivity test?