Question 2091 of 299 · NICET Fire Alarm Systems Level I
How is ground fault supervision of a circuit verified during acceptance testing?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2091
- B: Introduce a ground on a conductor and confirm the panel shows a trouble
Explanation
The test simulates a ground fault on each conductor to confirm the panel detects it and reports a trouble, then the fault is removed and the trouble should clear.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2092Within what time must a battery charger be able to recharge fully discharged fire alarm batteries?
- 2093A smoke detector is marked with a listed sensitivity range of 1.0 to 3.5 percent per foot obscuration. The test reads 3.9 percent per foot. What does this mean?
- 2094An addressable panel prints sensitivity readings for every smoke detector. May this be used for the required sensitivity test?
- 2095What qualification does NFPA 72 expect from people who inspect, test and maintain fire alarm systems?
- 2096Which statement about a Level I trainee performing tests is true?
- 2097A device fails its annual test and cannot be fixed the same day. What should the technician do?