Question 2111 of 299 · NICET Fire Alarm Systems Level I
Which pattern identifies a carbon monoxide alarm signal?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2111
- C: Temporal-4: four short pulses, then a pause
Explanation
CO alarms use the temporal-4 pattern, four 100 ms pulses followed by about 5 s of silence. Fire evacuation uses temporal-3.
More questions: Maintenance (Periodic Testing, Repair and Replacement)
- 2112What should the panel do when a single conventional smoke detector circuit goes into alarm and alarm verification is enabled?
- 2113What does a supervising station do with signals from a protected building?
- 2114After a fire alarm technician finishes a repair to field wiring, what testing is needed?
- 2115Which tool is best for measuring the current drawn by a NAC without opening the circuit?
- 2116A NAC carries 1.8 A in alarm and the voltage at the panel is 24 V. The total wire resistance out and back is 2.0 ohm. What voltage reaches the end of the circuit?
- 2117An initiating device circuit has a 3,900 ohm EOL resistor and 24 V across it. What supervisory current flows in normal standby, ignoring the detectors?