Question 2002 of 172 · Texas Fire Alarm License Exam
A fire alarm panel draws 0.45 A in standby and 2.8 A in alarm. Using 24 hours standby, 5 minutes alarm and the 20 percent safety margin required by NFPA 72 (2019), the minimum battery is about
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2002
- A: 13.2 Ah
Explanation
Standby 0.45 A x 24 h = 10.8 Ah. Alarm 2.8 A x 5/60 h = 0.23 Ah. Total 11.03 Ah x 1.2 = 13.2 Ah. Forgetting the safety margin gives 11.0 Ah. The 2022 edition replaced this 20 percent margin with a 1.25 aging factor.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2003An emergency voice/alarm communications system requires secondary power for 24 hours standby followed by how many minutes of alarm at maximum connected load?
- 2004A notification appliance circuit carries 1.5 A to the last appliance 400 ft from the panel on 14 AWG solid copper (about 3.07 ohms per 1,000 ft). The approximate voltage drop is
- 2005A 24 VDC initiating device circuit ends in a 4,700 ohm end-of-line resistor. The supervisory current through the resistor is about
- 2006Six strobes each draw 0.12 A and four horn/strobes each draw 0.16 A on one NAC. The total alarm current is
- 2007For public mode audible signaling, the evacuation signal should exceed the average ambient sound level by at least
- 2008A room has an average ambient sound level of 62 dBA. Under the public mode rule based on average ambient, the minimum audible signal level is