An emergency voice/alarm communications system requires secondary power for 24 hours standby followed by how many minutes of alarm at maximum connected load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2003
- B: 15 minutes
Explanation
Voice systems need 15 minutes of alarm operation at maximum connected load after 24 hours standby, compared with 5 minutes for a non-voice system.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2004A notification appliance circuit carries 1.5 A to the last appliance 400 ft from the panel on 14 AWG solid copper (about 3.07 ohms per 1,000 ft). The approximate voltage drop is
- 2005A 24 VDC initiating device circuit ends in a 4,700 ohm end-of-line resistor. The supervisory current through the resistor is about
- 2006Six strobes each draw 0.12 A and four horn/strobes each draw 0.16 A on one NAC. The total alarm current is
- 2007For public mode audible signaling, the evacuation signal should exceed the average ambient sound level by at least
- 2008A room has an average ambient sound level of 62 dBA. Under the public mode rule based on average ambient, the minimum audible signal level is
- 2009For private mode audible signaling, the signal must be at least how many dB above the average ambient sound level?