Question 2027 of 172 · Texas Fire Alarm License Exam

Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over

Exactly one answer is correct.

Show solution

Correct answer to question 2027

  • B: 2,000 cfm

Explanation

NFPA 90A requires supply side duct smoke detection for systems with a capacity greater than 2,000 cfm. 15,000 cfm is the threshold for return side detection in multistory systems.