Under the adopted NFPA 90A, smoke detectors in the supply air system are required downstream of filters and ahead of branch connections in air distribution systems over
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2027
- B: 2,000 cfm
Explanation
NFPA 90A requires supply side duct smoke detection for systems with a capacity greater than 2,000 cfm. 15,000 cfm is the threshold for return side detection in multistory systems.