Question 2028 of 172 · Texas Fire Alarm License Exam
The operable part of a manual fire alarm box must be mounted
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2028
- C: between 42 and 48 inches above the floor
Explanation
The operable part of each manual fire alarm box must be not less than 42 in. and not more than 48 in. above floor level.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2029Manual fire alarm boxes must be located within 5 feet of each exit doorway on each floor, and the travel distance to the nearest box must not exceed
- 2030How often must spot-type smoke detectors receive a functional test after acceptance?
- 2031Smoke detector sensitivity must be checked within one year after installation and then
- 2032Sprinkler waterflow alarm-initiating devices and valve supervisory switches are tested at what frequency under NFPA 72?
- 2033When performing the functional test of a smoke detector, the technician should
- 2034After a modification to an existing system, reacceptance testing must include all affected devices plus