Smoke detector sensitivity must be checked within one year after installation and then
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2031
- B: every alternate year
Explanation
Sensitivity is tested within 1 year after installation and every alternate year thereafter. After the second required test, the interval may be extended up to 5 years if the detectors stay in range.