Under NFPA 70 Article 760, the branch circuit disconnecting means for fire alarm equipment must be
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2044
- C: marked red, identified as FIRE ALARM CIRCUIT, and accessible only to qualified personnel
Explanation
The fire alarm branch circuit disconnect must have a red marking, be identified as FIRE ALARM CIRCUIT and be accessible only to qualified personnel. GFCI or AFCI protection is not allowed.