Question 2046 of 172 · Texas Fire Alarm License Exam
Power-limited fire alarm circuit conductors may NOT be placed in the same raceway with
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2046
- A: electric light, power and Class 1 conductors
Explanation
Article 760 requires PLFA circuits to be separated from electric light, power, Class 1 and non-power-limited fire alarm conductors, unless a listed barrier or other permitted method is used.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2047How often are restorable spot-type heat detectors functionally tested after acceptance?
- 2048A nonrestorable fixed-temperature spot-type heat detector is tested in service by
- 2049A projected beam smoke detector is functionally tested by
- 2050Where alarm verification is used for smoke detectors, the verification feature must not delay the reporting of an alarm by more than
- 2051Under positive alarm sequence, trained staff must acknowledge the alarm signal within
- 2052On a peaked ceiling, a row of spot-type smoke detectors must be located on or near the peak, within what horizontal distance of the peak?