Question 2045 of 172 · Texas Fire Alarm License Exam
Which cable type is required for power-limited fire alarm circuits installed in a plenum without a raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2045
- D: FPLP
Explanation
FPLP is the plenum rated power-limited fire alarm cable. FPLR is riser rated and FPL is general purpose.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2046Power-limited fire alarm circuit conductors may NOT be placed in the same raceway with
- 2047How often are restorable spot-type heat detectors functionally tested after acceptance?
- 2048A nonrestorable fixed-temperature spot-type heat detector is tested in service by
- 2049A projected beam smoke detector is functionally tested by
- 2050Where alarm verification is used for smoke detectors, the verification feature must not delay the reporting of an alarm by more than
- 2051Under positive alarm sequence, trained staff must acknowledge the alarm signal within