For NPLFA circuits, 18 AWG conductors must have overcurrent protection not exceeding
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2071
- B: 7 amperes
Explanation
Article 760 limits overcurrent protection for NPLFA conductors to 7 A for 18 AWG and 10 A for 16 AWG.